Can aluminum wire be used on AC/Furnace/Ranges ..........does the NEC address this anywhere? Thank you
ALLELECTRIC95 said:Can aluminum wire be used on AC/Furnace/Ranges ..........does the NEC address this anywhere? Thank you
infinity said:Some appliances are marked "use copper conductors only". Without that limitation, AL is fine.
macmikeman said:I've seen plenty of that, but it has me wondering if you transition the alum to copper conductors before connection to the appliance whip, would you meet the manufactures requirements now? Or do they mean copper all the way back to the breaker? I can't see them requiring this for other than the connection point of the appliance whip.
mc5w said:My wiring in aluminum ran cooler than Code said that it should have given the load and the ambient temperature. This is because I did as Dr. Jesse Aronstein suggested and used #220 silicon carbide paper to clean each individual strand, hit each strand with Ilsco Deox, then put all of the strands back together.