jmellc
Senior Member
- Location
- Durham, NC
- Occupation
- Facility Maintenance Tech. Licensed Electrician
One day I will not have to keep learning this lesson. I have had several jobs over the years to get very complicated because I took what the customer told me as fact.
This week I went to a student center at one of our local universities. Kitchen had a wall of receptacles out. Person in charge showed me the panel, far corner of building & said no breakers had tripped. Breakers 31, 33 and 35 were marked "kitchen counter", etc. 31 controlled the working receps & 33, 35 appeared to do nothing. I asked about other panels. He said there was 1 upstairs that fed nothing downstairs. I went there for good measure and found nothing. Found a couple of panels in the basement that only fed equipment there.
Kitchen had been a renovation, I could tell that. On opposite wall, I found boxes in cabinets, backs of cabinets cut out around them. Hard pipe out of floor, NM from boxes to receptacles. A few boxes had dead ended wires in them, so several changes over the years. An island had a box stubbed from floor & feeding 2 recepts there. So I began looking for hidden boxes on counter in question. Cut cabinet backs in several places, found nothing but the NM's from box to box. Found a hard pipe feeding down from clg with a black & red, only red hooked up, black dead ended. Asked director again about any other panels. "No there are no more". So I got out the fox & hound and tried getting signal at any panel. No luck. Finally found a ceiling hatch about 50 feet away. Fun crawl over a plaster ceiling on walk boards. Found conduit & traced it back TO A SECOND PANEL UPSTAIRS. I showed it to the guy and he was surprised. It was then he also told me there was also a kitchen upstairs. Then it was only a matter of replacing recepts with GFCI's and splitting circuits. Don't know why anyone set it up with just 1 when they had 2 available.
At any rate, misinformation turned a half day job into a day and a half. Never take someone's word for anything when the clues found tell a different story. I should have searched the building room by room for other panels. I was expecting to find buried receptacles that were burned out. I have seen that before.
The people running the building had bought it a few years ago from another group so did not fully know the history. Again, I should have looked for myself. I have also had maintenance men tell me they knew no one else had been working on this or that, then found out someone had. False information leads to a lot of wild goose chases.
This week I went to a student center at one of our local universities. Kitchen had a wall of receptacles out. Person in charge showed me the panel, far corner of building & said no breakers had tripped. Breakers 31, 33 and 35 were marked "kitchen counter", etc. 31 controlled the working receps & 33, 35 appeared to do nothing. I asked about other panels. He said there was 1 upstairs that fed nothing downstairs. I went there for good measure and found nothing. Found a couple of panels in the basement that only fed equipment there.
Kitchen had been a renovation, I could tell that. On opposite wall, I found boxes in cabinets, backs of cabinets cut out around them. Hard pipe out of floor, NM from boxes to receptacles. A few boxes had dead ended wires in them, so several changes over the years. An island had a box stubbed from floor & feeding 2 recepts there. So I began looking for hidden boxes on counter in question. Cut cabinet backs in several places, found nothing but the NM's from box to box. Found a hard pipe feeding down from clg with a black & red, only red hooked up, black dead ended. Asked director again about any other panels. "No there are no more". So I got out the fox & hound and tried getting signal at any panel. No luck. Finally found a ceiling hatch about 50 feet away. Fun crawl over a plaster ceiling on walk boards. Found conduit & traced it back TO A SECOND PANEL UPSTAIRS. I showed it to the guy and he was surprised. It was then he also told me there was also a kitchen upstairs. Then it was only a matter of replacing recepts with GFCI's and splitting circuits. Don't know why anyone set it up with just 1 when they had 2 available.
At any rate, misinformation turned a half day job into a day and a half. Never take someone's word for anything when the clues found tell a different story. I should have searched the building room by room for other panels. I was expecting to find buried receptacles that were burned out. I have seen that before.
The people running the building had bought it a few years ago from another group so did not fully know the history. Again, I should have looked for myself. I have also had maintenance men tell me they knew no one else had been working on this or that, then found out someone had. False information leads to a lot of wild goose chases.