I have run into a a situation with a tranformer this week that I thought I would share. We were lucky to catch this before suppling power.
A journeyman was hooking up a Tranformer (I'll not name MFG) and happen to notice that the leads from the core didn't seem to be in the correct position. The terminal lugs were in the marked position but the straps looked wrong. The X0 bonding terminal was correct but X's and H's seemed reversed.
To Masters verified it was incorrectly wired. Upon contacting Supplier Rep's and Manufacture Rep's the factory (in a nearby country, thank you NAFTA) verified that the wrong terminal board bar was installed at factory.
Does anybody else check the transformer wiring connections upon delivery before shipping truck leaves?
Check. Check. and Recheck.
A journeyman was hooking up a Tranformer (I'll not name MFG) and happen to notice that the leads from the core didn't seem to be in the correct position. The terminal lugs were in the marked position but the straps looked wrong. The X0 bonding terminal was correct but X's and H's seemed reversed.
To Masters verified it was incorrectly wired. Upon contacting Supplier Rep's and Manufacture Rep's the factory (in a nearby country, thank you NAFTA) verified that the wrong terminal board bar was installed at factory.
Does anybody else check the transformer wiring connections upon delivery before shipping truck leaves?
Check. Check. and Recheck.