Hi, can anyone please help me with this:given duplex 1600sqft each unit.each unit comes with: 11 kVA range,5A garbage disposal, 11A dishwasher, 4.5kVA water heater, 20KVA heater, 2-23A 240V air-conditioning units.use optional method to calculate feeder.My calcullation :
2units x 1600sqft x 3VA/sqft =9600VA
2x4500VA for 2small.appl+washing machine= 9000VA
then: 2x 11000VA range = 22000VA
2x 5Ax120 garab.disp = 1200VA
2x 11Ax120 dishwasher = 2640VA
2x4500VA(water heater) = 9000VA
-------------
53.440
-10.000 at 100%= 10.000VA
43.440 at 40% = 17.376VA
---------
27.376VA
heating/aircond.
2x20kW heater @ 65%= 26.000VA
2X2x23x240 @100%= 22.080VA omit
27.376+26.000=53.376VA
feeder=53.376/240
=222.4A
since I had this wrong at test where did I make mistake.Appreciate it.
This is second time I'm failing because I miscalculated duplex calculations again on optional method.Please help.