Background:
Weird (grandfathered) installation has a building with 2 incoming utility services. Call it Utility A (UA) and Utility B (UB). There is no tie between services. They are serving 2 separate areas of the building, each approximately 400kW. The project requires a generator to back up whole house in case of outage. So instead of one generator of 1MW, we go with 2 x 500kW generators, G1 and G2. One for each utility. At first, I was going to have a group mounted cb's in switchboard, to "take in" power from generator after paralleling, and then "feed" the transfer switches.
An idea came up to instead use 2 breakers for each generator, key interlocked for manual operation, so that G2 can be used to serve UA (which was the utility side being primarily served by G1) in case G1 fails or is under maintenance.
Question:
As a value engineering idea, can the switchboard really be removed and instead use TAP rule with a wireway above the transfer switches containing the tap lugs?
The thought is that this will remove the switchboard and the paralleling/synching operation of the generators and it will be less costly than original design of traditional multiple generators paralleling into a switchboard with multiple feeders to multiple ATS.
Question: