Attached sketch is gas pipe being used as grounding electrode?
What i understand in 250.50, the underground gas pipes/tanks are prohibited from being GEC, the OP doesn't mention the underground installation, also pipes inside building don't necessarily have a conductivity with underground services.
Am i missing something here ?
The tricky part is training the electrons to use the wire for bonding only.
Fortunately you are allowed/required to bond the gas pipe whether or not there is a dielectric union, and that is not considered as using it as a ground electrode.
Sent from my XT1585 using Tapatalk
When it changed, did you have to resize the bonding wire to become a GEC?Now that the old gas line at my shop is not one, it instantly turned into a GE.
And the EGC for whatever may energize the piping is all that is needed to make that bond.
CSST may have it's own additional rules that are outside the requirements of NEC.
In my area the new gas services are HPDE. Before that they were PVC coated iron pipe. I got a couple of sections for a closet rod, strong, quiet, and slick.
And the gas company has cathodic protection on the gas mains, seems like if you bond to it, they know and will find you.
One clarification: the fault current which causes pinhole damage to CSST is lightning induced current, not line fault current. Lightning induced (not necessarily direct strike) current has high frequency components and orders of magnitude greater current compared to line faults.The appliance EGC assures that the piping on the "load side" of the CSST is grounded. The reason for bonding a gas piping system is to make sure that the piping on the "line side" of the CSST is equally grounded, so the CSST is never subject to having to carry a fault current.