Dear friends,
As you all know we can select one size up breaker if 125% of continues+100% non continues loads fall between two standard ratings. for example, if the continues load is 37 A then 125% of 37 will be 46.25 A which is between 45 A and 50 A and I can select 50 A breaker to protect my circuit.
My question is what if I select a bigger size breaker for example in above example I select a 60 or 70 or even a 100 A breaker, am I violating the code provided that I size the cable according to breaker rating?
I think as long as I size the cable based on the breaker rating I am on safe side because the breaker is there to protect the cable not the load.
Thank you for your responses in advance.