PCN
Senior Member
- Location
- New England
Is there anything in the code that clarifies ambient temperature?
On a current project the inspector claims we have not applied the proper correction factor when sizing conductors for rooftop equipment. (conduit routed on roof on 4" blocks). In 310.16 I used the 60c column with a 0.71 correction factor which is 105-113 degrees f. The inspector feels that with a black membrane flat roof the temperature will exceed that. While I don't completely disagree with him, I'm not really buying it 100%. I've worked on many a roof and know they get hot in the summer but what correction factor is well....correct?
Project is in New England.
On a current project the inspector claims we have not applied the proper correction factor when sizing conductors for rooftop equipment. (conduit routed on roof on 4" blocks). In 310.16 I used the 60c column with a 0.71 correction factor which is 105-113 degrees f. The inspector feels that with a black membrane flat roof the temperature will exceed that. While I don't completely disagree with him, I'm not really buying it 100%. I've worked on many a roof and know they get hot in the summer but what correction factor is well....correct?
Project is in New England.