A new problem has appeared in the 2011 code: The formula for ampacity corrected for a different ambient temperature than in table 310.15B(16) uses a value Tc called "temperature rating of conductor".
However, this is misleading. People are plugging in 90 degrees there for THHN or THWN-2. This is wrong. The value Tc is not the conductor temperature RATING, but rather is the DESIRED conductor operating temperature.
This problem arises when using THHN connected to 75 degree terminals. Since you cannot allow the temperature of the THHN to exceed 75 degrees, even though the wire would be happy (but the teminal would not); you have to use 75 degrees for Tc and use the ampcity for 75 degrees from table 310.15-B(16) even though THHN is not listed in the 75 degree column.
So those who insist on blindly following the Code like the devil reads the Bible are going to plug in 90 degrees for THHN come what may.
The problem is actually more general and related to the headings of the colmuns in table 310-15B(16). The temperature colmns should not be given the heading "Temperature rating of conductor" but rather the heading should be "Desired conductor operating temperature". The values 60, 75 and 90 degrees indicate how hot the conductor will get when passing the indicated number of amps, whatever the "rating" of the wire.
I recommend changing the definition of Tc in 310.15B(2) to
"Tc = Desired conductor operating temperature"
and likewise changing the heading of table 310.15B(16) to the same words
However, this is misleading. People are plugging in 90 degrees there for THHN or THWN-2. This is wrong. The value Tc is not the conductor temperature RATING, but rather is the DESIRED conductor operating temperature.
This problem arises when using THHN connected to 75 degree terminals. Since you cannot allow the temperature of the THHN to exceed 75 degrees, even though the wire would be happy (but the teminal would not); you have to use 75 degrees for Tc and use the ampcity for 75 degrees from table 310.15-B(16) even though THHN is not listed in the 75 degree column.
So those who insist on blindly following the Code like the devil reads the Bible are going to plug in 90 degrees for THHN come what may.
The problem is actually more general and related to the headings of the colmuns in table 310-15B(16). The temperature colmns should not be given the heading "Temperature rating of conductor" but rather the heading should be "Desired conductor operating temperature". The values 60, 75 and 90 degrees indicate how hot the conductor will get when passing the indicated number of amps, whatever the "rating" of the wire.
I recommend changing the definition of Tc in 310.15B(2) to
"Tc = Desired conductor operating temperature"
and likewise changing the heading of table 310.15B(16) to the same words