Ambient Temperature Correction factors

Status
Not open for further replies.

minesh21

Senior Member
Location
CA USA
I am running conductors in conduit outdoors (not underground) and would like to apply the ambient temperature correction factors in Table 310.15(B)(2)(a). Problem is the NEC doesn't specifically state HOW the ambient temperature is found. Any suggestions? Any tables or websites I could use?
 
310.15(B)(3)(5) Informational Note:

Informational Note: One source for the ambient temperatures
in various locations is the ASHRAE Handbook — Fundamentals.
 
I've heard a few different interpretations, one says that you use the yearly average temperature.
 