Ambient Temperature for Underground Ductbanks

Status
Not open for further replies.

FaradayFF

Senior Member
Location
California
Hi Gents,

Typically we adjust cable ampacity based on ambient air temperature, but for cables installed in underground ductbanks, I don't think we have to worry about it, because the temperature is lower than 40 degree C. Am I correct on this?

Thanks,
EE
 

ron

Senior Member
We do Neher McGrath calculations for UG ductbanks per Annex B
That mostly adjusts for the inability for the earth or surrounding material to release heat like it would if it were above ground
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
In my opinion, the captive air [ in a duct] temperature [usually 60oC] it has a small influence on ampacity. However, the main temperature drop it is from outside of the duct bank to Earth. The calculation can follow Neher &McGrath way- up-dated in IEEE 835/1994 [or IEC 60287].
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
Sorry. Wrong sentence. The temperature drop on duct air is about 45% but the air temperature does not so important[+/-3-5% from 55 to 75oC]. The approximate 40% of the total temperature drop it is the temperature drop from the outside surface of the duct [to the earth including the concrete]
 