mwm1752
- Aspen, Colo
Wow. How cool. Rooftops get hot. Who knew?
Good thing the Copper Development Assc. has a chart to tell us how to know how much more copper we need to use for rooftop installations.
Don is a classy guy and made my point more elegantly than I did.Got 3 things out of your comments -- you know the formula for 2% design, you don't care, or you don't derate. FYI, answers a a good thing when tradesmen ask questions prior to install.
Kind of blows a hole in all ampacity adjustment procedures then doesn't it? If it is heat that is supposed to degrade the conductors, why are they not failing on these rooftops where the temp's are fairly extreme sometimes?The study was funded by the copper association and there is no history of cable failures on roof top installations to back up the copper associations study. It appears to me and many others that the study is just aggressive marketing.
Very good point.Kind of blows a hole in all ampacity adjustment procedures then doesn't it? If it is heat that is supposed to degrade the conductors, why are they not failing on these rooftops where the temp's are fairly extreme sometimes?
We all know you mean 310.15(B)(3)(c) Exception. There is no exception to 310.15(B)(3)(a)(5)(c).Very good point.
I wonder if the exception for XHHW in 310.15(B)(3)(a)(5)(c) will be extended to other derating applications?
That's what I get for trying to follow the code sections in the electronic version of the handbook. The commentary gets in the way of following the sections...I knew I should have looked at my hard copy of the code itself....We all know you mean 310.15(B)(3)(c) Exception. There is no exception to 310.15(B)(3)(a)(5)(c).
I don't use the handbook very often, but I see what you mean. The indentation for 3rd level subordinates (parenthesized lower-case alphabetic) is greater than 4th level subordinates (parenthesized numeric). Indentation, when used, should increase with level.That's what I get for trying to follow the code sections in the electronic version of the handbook. The commentary gets in the way of following the sections...I knew I should have looked at my hard copy of the code itself....
And should be the same as in the print version, independent of the PDF reader used for the electronic version. Anybody have the print version of the Handbook to check?Indentation, when used, should increase with level.
Some of us forgot how to use a real bookAnd should be the same as in the print version, independent of the PDF reader used for the electronic version. Anybody have the print version of the Handbook to check?
I only have the handbook in the electronic version. My code book is out in the truck and usually am too lazy to go look at it. I need a way to view the electronic handbook without seeing the commentary text, but I don't know how to do that.I don't use the handbook very often, but I see what you mean. The indentation for 3rd level subordinates (parenthesized lower-case alphabetic) is greater than 4th level subordinates (parenthesized numeric). Indentation, when used, should increase with level.
Is that electronic version a PDF version, that appears to be the only way they offer the handbook in an electronic format.I only have the handbook in the electronic version. My code book is out in the truck and usually am too lazy to go look at it. I need a way to view the electronic handbook without seeing the commentary text, but I don't know how to do that.
I don't believe it is possible. If you want to view current edition [2014], you can use the online NEC Public Input... but to copy and paste you have go into edit mode. For older editions, you'll have to resort to other means. If you're too lazy to go get your code book out of the truck, I'd advise not trying to use the NFPA online viewer. Perhaps the following link will help:... I need a way to view the electronic handbook without seeing the commentary text, but I don't know how to do that.
https://archive.org/details/gov.law.nfpa.nec.2011
The same site has the 2014 edition:I have PDFs of the 99 through 2011 with just the code text. The only hand book I have is the 2014...not really sure why I bought it as I don't normally buy the handbook.