1.) NEC Section/Paragraph: 310.15(B)(6) text
2.) Proposal Recommends: [revised text]
3.) Proposal: Amend text to read:
Conductors shall be permitted to be connected to equipment rated according to Table 310.15(B)(6) under the following conditions:
(a) The supply is a single phase, 120/240 Volt, 3 wire system.
(b) The conductors are installed for one-family, two family, and multifamily dwellings
(c) The conductors are service laterals, service entrance conductors, and/or feeders that serve only one individual dwelling unit.
(d) These conductors shall serve as the main power feeder to each dwelling unit.
(e) These conductors shall serve lighting and appliance branch-circuit panelboards.
For the purposes of this section, the main power feeder shall be the feeder(s) between the main disconnect and the panelboard(s). The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements of 215.2, 220.61, 230.42 are met.
4.) Substantiation: As the text currently stands, the first sentence of this section is very difficult to read, containing 56 words seperated by no less than nine commas. This section is packed with various requirements. It would be much clearer to understand and more readily and accurately applied in a list format. It is very easy to misapply this section as it currently stands.
In addition, given the general hierarchy of overcurrent protection and conductor installation, the sentence that allows feeders to not be larger than the service conductors is unnecessary. If such an improbable installation were to occur, then it's reasonable to require the conductor ampacities given in subsequent tables to apply.
So how's about that?
[ July 21, 2005, 07:52 PM: Message edited by: georgestolz ]
2.) Proposal Recommends: [revised text]
3.) Proposal: Amend text to read:
Conductors shall be permitted to be connected to equipment rated according to Table 310.15(B)(6) under the following conditions:
(a) The supply is a single phase, 120/240 Volt, 3 wire system.
(b) The conductors are installed for one-family, two family, and multifamily dwellings
(c) The conductors are service laterals, service entrance conductors, and/or feeders that serve only one individual dwelling unit.
(d) These conductors shall serve as the main power feeder to each dwelling unit.
(e) These conductors shall serve lighting and appliance branch-circuit panelboards.
For the purposes of this section, the main power feeder shall be the feeder(s) between the main disconnect and the panelboard(s). The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements of 215.2, 220.61, 230.42 are met.
4.) Substantiation: As the text currently stands, the first sentence of this section is very difficult to read, containing 56 words seperated by no less than nine commas. This section is packed with various requirements. It would be much clearer to understand and more readily and accurately applied in a list format. It is very easy to misapply this section as it currently stands.
In addition, given the general hierarchy of overcurrent protection and conductor installation, the sentence that allows feeders to not be larger than the service conductors is unnecessary. If such an improbable installation were to occur, then it's reasonable to require the conductor ampacities given in subsequent tables to apply.
So how's about that?