I agree with Bryan for a single phase transformer, but not for a three phase transformer. The way I remember it is to calculate the full load current of the transformer and then divide that by the impedance as a decimal, not in percent.
Jim T
Re: Amnesia
"Z" in this case does not carry the units of impedance. It is per unit impedance, Zpu, expressed as a decimal fraction. The formula computes the rated current from the KVA rating and then multiplies the rated current by the inverse of the per unit impedance. That is:
Zpu = Ir(A) x Z(Ohms) / Vr(V); by definition,
1 = Iss(A) x Z(Ohms) / Vr(V); short circuit condition,
Dividing one equation by the other yields,
Iss(A) = Ir(A)/Zpu = (KVA/Vr)/Zpu
Where Iss is the short circuit current, Ir is the rated current, and Vr is the rated voltage.
OK?
[ September 12, 2005, 09:16 PM: Message edited by: rattus ]