Hello,
I am new here and have a question that seems to be an odd one.
Cannot go into complete specifics but will offer up as much info as possible.
In an office building type setting using a wireway how many Conductors total can be put into a wireway before deration begins? I want to say 30 plus grounds (15 line, 15 neutral, then 15 grounds for 45) . Each circuit includes its own neutral and ground. Would this assumption be correct or am I way off? I know you have 20% fill to deal with but that's not the topic in hand. Reading the below text has me leaning more towards 30 line, 30 neutral, 30 ground.
This is pulled from the NEC 2008 (only digital copy I currently have)
This is from 376.22
(B)Adjustment Factors. The adjustment factors in
310.15(B)(2)(a)shall be applied only where the number of
current-carryingconductors, including neutral conductors
classifiedas current-carrying under the provisions of
310.15(B)(4),exceeds 30. Conductors for signaling circuits
orcontroller conductors between a motor and its starter and
used onlyfor starting duty shall not be considered as
current-carryingconductors.
This is from 310.15(B)(4)
(a) Aneutral conductor that carries only the unbalanced
current fromother conductors of the same circuit
shall not berequired to be counted when applying the provisions
of310.15(B)(2)(a).
Table 310.15(B)(2)(a) Adjustment Factors for More Than
Three Current-Carrying Conductors in a Raceway or Cable
Number of
Current-Carrying
Conductors
Percent of Values in Tables
310.16 through 310.19 as
Adjusted for Ambient
Temperature if Necessary
4?6 80
7?9 70
10?20 50
21?30 45
31?40 40
41 and above 35
I am new here and have a question that seems to be an odd one.
Cannot go into complete specifics but will offer up as much info as possible.
In an office building type setting using a wireway how many Conductors total can be put into a wireway before deration begins? I want to say 30 plus grounds (15 line, 15 neutral, then 15 grounds for 45) . Each circuit includes its own neutral and ground. Would this assumption be correct or am I way off? I know you have 20% fill to deal with but that's not the topic in hand. Reading the below text has me leaning more towards 30 line, 30 neutral, 30 ground.
This is pulled from the NEC 2008 (only digital copy I currently have)
This is from 376.22
(B)Adjustment Factors. The adjustment factors in
310.15(B)(2)(a)shall be applied only where the number of
current-carryingconductors, including neutral conductors
classifiedas current-carrying under the provisions of
310.15(B)(4),exceeds 30. Conductors for signaling circuits
orcontroller conductors between a motor and its starter and
used onlyfor starting duty shall not be considered as
current-carryingconductors.
This is from 310.15(B)(4)
(a) Aneutral conductor that carries only the unbalanced
current fromother conductors of the same circuit
shall not berequired to be counted when applying the provisions
of310.15(B)(2)(a).
Table 310.15(B)(2)(a) Adjustment Factors for More Than
Three Current-Carrying Conductors in a Raceway or Cable
Number of
Current-Carrying
Conductors
Percent of Values in Tables
310.16 through 310.19 as
Adjusted for Ambient
Temperature if Necessary
4?6 80
7?9 70
10?20 50
21?30 45
31?40 40
41 and above 35