AMP Draw varying with RPM

Status
Not open for further replies.
Hello, we are running a compressor with a 125hp 460v 1800rpm electric motor. We have a VFD varying the speed of the motor. My question is about the amp draw as the rpm varies. We are operating between 1400 and 1800 rpm. Assuming the load is constant should we see a reduction in amp draw as rpm decreases or should the amp draw be constant?
 

Besoeker

Senior Member
Location
UK
Hello, we are running a compressor with a 125hp 460v 1800rpm electric motor. We have a VFD varying the speed of the motor. My question is about the amp draw as the rpm varies. We are operating between 1400 and 1800 rpm. Assuming the load is constant should we see a reduction in amp draw as rpm decreases or should the amp draw be constant?
Depends on the type of compressor.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Depends on the type of compressor.
What he said.

Basically if it is any type of Positive Displacement compressor, like a reciprocal, screw, lobed, scroll, diaphragm compressor etc., then the amps would stay relatively constant (there is some slight reduction as mechanical losses decrease a little with speed in some designs). These are what's called "Constant Torque" loads, meaning that regardless of speed, the torque required by the machine stays relatively constant, and torque = current for the most part.

If it is however a CENTRIFUGAL compressor, aka "Radial Compressor", then the amps would decrease with speed, and a rate greater than the speed change based on the Affinity Law for centrifugal loads wherein power to drive the load varies at the cube of the speed change. Note that I said "power", as in kW, not Amps, but Amps go down too.
 

kwired

Electron manager
Location
NE Nebraska
From motor's perspective, less speed will ordinarily translate to less mechanical output power.

Normally the drive output voltage is still proportional (or close to proportional) to frequency, so if design full speed is 460 volts and 60 Hz, then running at 30 Hz will have output voltage of 230. To get same proportional output torque current will still be same as it is at 460V 60Hz. This voltage/current level still gives you around half the input power when output power is halved, mechanical differences at the two speeds will vary the actual values.
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
It also depends on which amp draw you're talking about.
The current into the VFD will drop with the motor speed.

p.s: The load isn't constant. It's roughly proportional to the motor speed.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
It also depends on which amp draw you're talking about.
The current into the VFD will drop with the motor speed.
....
This is a good point nonetheless. "Amp draw" becomes a bit too vague when a VFD is involved, because the amp draw from the MOTOR will be different from the amp draw from the LINE. You need to specify which side of the VFD you are wanting to know about.
 
Thank you all for the responses. We are running a rotary screw compressor and measuring it on the output side of the VFD. I apologize for not giving full information! You're responses have definitely helped me.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Thank you all for the responses. We are running a rotary screw compressor and measuring it on the output side of the VFD. I apologize for not giving full information! You're responses have definitely helped me.
So what are you seeing on the output side of the drive to the screw as you vary the speed?
 

retirede

Senior Member
Location
Illinois
Thank you all for the responses. We are running a rotary screw compressor and measuring it on the output side of the VFD. I apologize for not giving full information! You're responses have definitely helped me.

This gets more complicated. If the air demand is constant and the compressor was partially loaded at full speed, the throttling mechanism will try to increase the flow of the compressor as you slow it down. So the torque required by the compressor will rise accordingly. How much it rises depends on the type of control mechanism.
 