Amp meter

Status
Not open for further replies.

hardworker

Senior Member
400amp commercial service, that may be getting close to capacity -- What type of metering device, will give me a continual read-out of the actual amps being drawn?

I would like to see the peak times, that are using the most amps and the valley times, that are using the least.
 
You need a recording meter and you need to leave it in place for quite while. I think the NEC wants a month but I am really not sure about that.

We used to rent them when we needed them now we own one.
 
You need a recording meter and you need to leave it in place for quite while. I think the NEC wants a month but I am really not sure about that.

We used to rent them when we needed them now we own one.


220.87 Determining Existing Loads.
The calculation of a feeder or service load for existing installations shall be permitted to use actual maximum demand to determine the existing load under all of the following conditions:
(1) The maximum demand data is available for a 1-year period.
Exception: If the maximum demand data for a 1-year period is not available, the calculated load shall be permitted to be based on the maximum demand (measure of average power demand over a 15-minute period) continuously recorded over a minimum 30-day period using a recording ammeter or power meter connected to the highest loaded phase of the feeder or service, based on the initial loading at the start of the recording. The recording shall reflect the maximum demand of the feeder or service by being taken when the building or space is occupied and shall include by measurement or calculation the larger of the heating or cooling equipment load, and other loads that may be periodic in nature due to seasonal or similar conditions.
(2) The maximum demand at 125 percent plus the new load does not exceed the ampacity of the feeder or rating of the service.
(3) The feeder has overcurrent protection in accordance with 240.4, and the service has overload protection in accordance with 230.90.
 