goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
Can an Amp-probe measure amperage properly when clamped onto parallel conductors ?
The reason I ask this is because I had a power quality problem at an office complex where several 3-phase roof-top AC units were blowing (only 1) 30 amp fuse during the hot summer months. I checked every possible connection I could find right down to the service entrance and all were tight and properly terminated. While I was at one of the roof-top units in August I had my (analog) amp-probe clamped onto the leg that was giving us a problem and the AC guy had his (digital) probe clamped onto the same phase and all was well at around 18 amps. Suddenly and mysteriously my meter read 40 amps for about 30 seconds while the AC guy's did not change. I also checked the voltage (phase to phase) at that point in time and there was no significant change.
I contacted the POCO and they came out to the job to install a test meter at the service entrance. They believe (as I do) that there is probably a piece of equipment that is going bad somewhere inside the building. However, this is an 800 amp, 3-phase, 120/208 service with parallel 350 MCM cables. They clamped their meter leads across the parallel feeders and assured me that the readings would be accurate. I always thought that an amp-probe measured amperage based on induction of single conductors. Am I incorrect or is it done by heat or some other measuring method ?
If anyone has experienced this or knows the answers to either question would you please post and enlighten me.
Thanks,
Phil,
Gold Star Electric
New Jersey
The reason I ask this is because I had a power quality problem at an office complex where several 3-phase roof-top AC units were blowing (only 1) 30 amp fuse during the hot summer months. I checked every possible connection I could find right down to the service entrance and all were tight and properly terminated. While I was at one of the roof-top units in August I had my (analog) amp-probe clamped onto the leg that was giving us a problem and the AC guy had his (digital) probe clamped onto the same phase and all was well at around 18 amps. Suddenly and mysteriously my meter read 40 amps for about 30 seconds while the AC guy's did not change. I also checked the voltage (phase to phase) at that point in time and there was no significant change.
I contacted the POCO and they came out to the job to install a test meter at the service entrance. They believe (as I do) that there is probably a piece of equipment that is going bad somewhere inside the building. However, this is an 800 amp, 3-phase, 120/208 service with parallel 350 MCM cables. They clamped their meter leads across the parallel feeders and assured me that the readings would be accurate. I always thought that an amp-probe measured amperage based on induction of single conductors. Am I incorrect or is it done by heat or some other measuring method ?
If anyone has experienced this or knows the answers to either question would you please post and enlighten me.
Thanks,
Phil,
Gold Star Electric
New Jersey