mkgrady
Senior Member
- Location
- Massachusetts
I get confused by the tables for allowable amperage for the smaller wires (14, 12 and #10). I understand the ratings are before any derating factors for ambient temperature and more than 3 CCC in a raceway. And that the breaker size can't be larger than 15, 20 and 30 amps.
My confusion comes in when it is a motor load. which is an exception to the 15, 20, 30 amp limit. Say for example an HVAC unit has an MCA of 22 amp and a MOCP of 25. Are there any circumstances that would allow the wire size of any type to be #12?
My confusion comes in when it is a motor load. which is an exception to the 15, 20, 30 amp limit. Say for example an HVAC unit has an MCA of 22 amp and a MOCP of 25. Are there any circumstances that would allow the wire size of any type to be #12?