Can any one help me with which table to use for 200 amp sub feed conductors? Table 310.15(B)(6) or 310.16.
is 4/0 aluminum gould for 200 amp? Thank
is 4/0 aluminum gould for 200 amp? Thank
pparry7@yahoo.com said:Can any one help me with which table to use for 200 amp sub feed conductors? Table 310.15(B)(6) or 310.16.
is 4/0 aluminum gould for 200 amp? Thank
pparry7@yahoo.com said:whats the deal with 4/0 ser cable bieng rated at 200 amps? thats what we use for 90% of are sub feeds but I have a job with 2" pvc feeding a 200amp 120/v 240/v sub panel 250 mcm put's over my wire fill.
pparry7@yahoo.com said:I have a job with 2" pvc feeding a 200amp 120/v 240/v sub panel 250 mcm put's over my wire fill.
roger said:4/0 SER is not rated for 200 amps, see table 310.16.
It is allowed to be used for a 200 amp 120/240-Volt, 3-Wire, Single-Phase Dwelling Service, but this does not mean it is a 200 amp cable. See the text in 310.15(B)(6) as 480 Sparky mentions.
90% of your sub-feeds are in violation.
Roger
tryinghard said:Looks to me like 4/0 SER al is rated at 150A, see 338-10 & 334-80. I think this could be a problem if one uses a "farm" type 200A residential panel, it has feed thru lugs and about 8 space distribution, it would be easy to just run 4/0 SER to a sub panel but this sounds like a violation if the farm panel is mounted on the house.
:-?
Dennis Alwon said:As of 2008 ser must be use at 60C if it is used for interior wiring. 2005 still allows 90C
infinity said:#4/0 Al is rated for 180 amps. Those sub feeds would be a violation if the connected load was greater than 180 amps and protected at 200 amps. However #4/0 Al can be used to feed a subpanel if the connected load is 180 amps or less. This is due to the fact that 180 amps is not a standard size listed in 240.6 so the next standard size (200 amps) maybe used. This is under the 2005 NEC.
tryinghard said:Are you sure that's not the way I understood 338-10 & 334-80, so my post included 60 degree column
tryinghard said:Looks to me like 4/0 SER al is rated at 150A, see 338-10 & 334-80. I think this could be a problem if one uses a "farm" type 200A residential panel, it has feed thru lugs and about 8 space distribution, it would be easy to just run 4/0 SER to a sub panel but this sounds like a violation if the farm panel is mounted on the house.
(4) Installation Methods for Branch Circuits and Feeders
(a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Parts I and II of Article 334, excluding 334.80.
(4) Installation Methods for Branch Circuits and Feeders.
(a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Part II of Article 334.
Dennis Alwon said:2005 NEC art. 338.10 says excluding 334.80 however the 2008 omits the words "excluding 334.80"
tryinghard said:Trevor,
How does this line up with 240-4(B)? If I have a calculated load at 195A I understand I can use a 200A OCPD with the 4/0 Al at 75?
infinity said:It's simple your calculated load cannot exceed the ampacity of the conductor. Under the 2005 SE cable can be used at 75 degrees C which would make it's ampacity 180 amps. You cannot protect this at 200 amps if the calculated load is 195 amps. You will need a larger conductor.
tryinghard said:Well 240-4(B) allows me to.
tryinghard said:Trevor,
How does this line up with 240-4(B)? If I have a calculated load at 195A I understand I can use a 200A OCPD with the 4/0 Al at 75?
iwire said:No, read what Rob said, 240.4(B) allows you to use a 200 amp breaker, it does not allow you load the cable past it's rated ampacity.
infinity said:It's simple your calculated load cannot exceed the ampacity of the conductor. Under the 2005 SE cable can be used at 75 degrees C which would make it's ampacity 180 amps. You cannot protect this at 200 amps if the calculated load is 195 amps. You will need a larger conductor.