I have a customer specifying the use of 535MCM loco cable. The only info I can get from the manufacturer on the load rating of the cable is that it is good for 730 amps in free air.
I will have 4-6 of these in each conduit. My question is how do I derate? I know I have to derate table 310-16 ampacities which already covers (3) current carrying conductors by 80% to cover more than three conductors in the conduit. Since I don't have a conduit rating for the 535 Loco cable is there any additional derating that has to be considered other than normal for temperature compensation?
I will have 4-6 of these in each conduit. My question is how do I derate? I know I have to derate table 310-16 ampacities which already covers (3) current carrying conductors by 80% to cover more than three conductors in the conduit. Since I don't have a conduit rating for the 535 Loco cable is there any additional derating that has to be considered other than normal for temperature compensation?