Wanting to be sure I have this correct, say I have four 30 amp circuits in a raceway (8ccc) 90c degree conductors. After ampacity adjustments (40x70%=28) my ungrounded conductors are now only good for 28amperes.
After this is applied is the next size up rule still allowed to be used and I could still use a 30amp OCPD, if all the requirements are met to do so?
OCPDs rated 800A or less. If you meet the three requirements of 240.4(B), you can use the next higher standard rating of OCPD listed in 240.6 (above the ampacity of the ungrounded conductors being protected).