Okay just want to check my knowledge on this as it turned into a flame thread elsewhere on the internet. *cough* reddit.
So derating/adjusting romex through holes in resi construction.
Say you have 4 12/2 romex cables, so 8 current carrying conductors
310.15(B)(16)
7 to 9 conductors = 70% adjustment
12 gauge 90 degree c wire is 30A
so 30 * .7 =21A
Great!
But what if the terminals are 75deg c? My read on 110.14(C) specifically the second sentence "
Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both."
Means you don't have to take the terminal into account for bundling adjustment. To me this makes sense as the threat is heat at the bundling point. You're still sizing the overall conductor for the 75deg c column for overall current capacity. Just double checking with the hive mind.
So derating/adjusting romex through holes in resi construction.
Say you have 4 12/2 romex cables, so 8 current carrying conductors
310.15(B)(16)
7 to 9 conductors = 70% adjustment
12 gauge 90 degree c wire is 30A
so 30 * .7 =21A
Great!
But what if the terminals are 75deg c? My read on 110.14(C) specifically the second sentence "
Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both."
Means you don't have to take the terminal into account for bundling adjustment. To me this makes sense as the threat is heat at the bundling point. You're still sizing the overall conductor for the 75deg c column for overall current capacity. Just double checking with the hive mind.