When adjusting amapacity due to # CCC in raceway or ambient temp you don't use 125% even if it's a continious load?
You are correct. The 125% for continuous load is not used for adjustment or correction factors.When adjusting amapacity due to # CCC in raceway or ambient temp you don't use 125% even if it's a continious load?
These statements are not true.The derated ampacity must be equal or greater than the continuous load required ampacity
If you have a 40 amp continuous load you need a conductor with a 50 amp ampacity after derating
The ampacity after derating only has to be 41A. So in your example, you could further have a 50C ambient temperature (0.82 correction factor for 90C rated insulation) for a final ampacity of 75A * 0.7 CCCs * 0.82 temperature = 43A.For example if you had a 40 amp continuous load and 8 #6 THWN-2 in a conduit you could use the 75 amp 90 deg for derating to 52 amps and be o.,k. based on a 50 amp load.
The ampacity needs to be 40A (the maximum load to be served) after the application of any adjustment or correction factors. That's part (b) in what you posted.If he has a 40 amp continuous load the ampacity of the conductor would need to be 50 amps.
210.19:.........not less than the larger of 210.19(A)(1)(a) or (b). (a) Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load. (b) The minimum branch-circuit conductor size shall have an allowable ampacity not less than the maximum load to be served after the application of any adjustment or correction factors.
Not in the Article 100 sense. Let me make explicit the implicit meaning of 210.19 for you:If he has a 40 amp continuous load the ampacity of the conductor would need to be 50 amps.
The 2011 NEC's version of 210.19(A)(1) was clearer:[This section's text could be improved.]
If this is 2023, then great, it's fixed. 2020, which we're on now, is horrid.Not in the Article 100 sense.......
No, it's not. If you read what I wrote, the first bolded text in that quote is my insertion; that bolded text is not in the NEC. But it is implied by the second bolded text.If this is 2023, then great, it's fixed.
Yes, and this is why you apply the 125% continuous factor for the termination check, which uses the termination temperature tabular ampacity without any adjustment or correction. And when doing the "run of the wire" check, which uses the insulation temperature ampacity with adjustment and correction, no 125% continuous factor is required.My understanding is the reasoning for 125% for continuous loads was always for termination ratings of standard overcurrent devices, and the reason why you don't need to apply that 125% for 100% rated devices.
Alright, so I still don't understand (per the strict reading of the 2020 at least) how "in accordance with 310.14" means "before the application of any adjustment or correction factors", when 310.14(A)(3)'s informational note tells you that (A)(3) more or less requires 310.15's deratings. I know INs aren't enforceable, but I'd never just wave that clear of one away anywhere else in the book; it's basically saying "hey you! we mean go to the next section right now!"No, it's not. If you read what I wrote, the first bolded text in that quote is my insertion; that bolded text is not in the NEC. But it is implied by the second bolded text.
Cheers, Wayne
Yeah, again, it's terrible wording. If you read 210.19(A)(1)(a) in isolation, the language obviously would mean that you do apply correction and adjustment factors.Alright, so I still don't understand (per the strict reading of the 2020 at least) how "in accordance with 310.14" means "before the application of any adjustment or correction factors", when 310.14(A)(3)'s informational note tells you that (A)(3) more or less requires 310.15's deratings.
You basically have it correct, but let me elaborate on your answers:You have me confused also.
If you have a 25A continuous load, then 210.19(A)(1)(a) (and the similar sections for feeders and SECs) says that at the terminations you need an unadjusted and uncorrected ampacity of at least 31.25A. That would be using the table column for the termination temperature, typically 75C, occasionally 60C.a.) I have a 25 amp load that would be 31.25 after the 125% for continuous load was added.
If you have a 25A load, continuous or non-continuous, doesn't matter, then 210.19(A)(1)(b) (and the similar sections for feeders and SECs) says that you need a conductor with a final ampacity of 25A. With a 0.7 adjustment factor and no temperature correction, that means you can use the table column for the conductor insulation temperature, typically the 90C column, and look for a conductor that is at least 35.7A in that column.b.) I have the same 25 amp load but I have an adjustment factor of 70% because of number of conductors in a conduit. 25/.7 = 35.7 amps
This means I need a conductor good for 35.7 amps