I have a question regarding ampacity and conditions of use on a PV source circuit. Ultimately I am trying to determine wire size -
Say I have a string of modules. The way I generally size my PV source circuit wire is this - Isc x 1.25 (for increased irradiance) x 1.25 (for 80% ampacity rule); we will call this "min ampacity". I then do a second calculation to find "adjusted ampacity" using conditions of use calculations - Isc x 1.25(for increased irradiance) x temp. derate factor x conduit fill derate factor.
I then compare "min ampacity" value to "adjusted ampacity" and use the larger of the two as my ampacity to size the wire.
However, I have been wondering why the 80% ampacity rule is not taken into account when derating for conditions of us... in essence, conditions of use are changing the ampacity. So why would the 80% rule not apply after derating ampacity for conditions of use?