I have 4#12 phase and 4#12 neutral in one conduit for system furniture at 120V single phase fed from 20A breaker. System furniture load for each circuit is 4.1A.
Based on Table 310.15(B)(3)(a) my correction factor is 0.7 with 8 current carrying conductors. With #12 ampacity is derated to 14A.
Would not either the breaker need to be changed to 15A or cable changed from#12 to #10 awg?