I have a ground faulted 1750mcm cable that is part of a 2000 amp feeder circuit. The existing circuit uses two 1750mcm cables per phase. We will probably replace all 6 cables due to the fact that they are 20 years old and we will probably damage them if we just try to replace the single bad cable. This cable isn't readily available and has very long manufacture lead times, not to mention a 10,000' minimum order. I am considering using 4 runs of 1000mcm per phase to replace the original circuit. 1000mcm is common and can be delivered right away at the lengths we need. My question is, how do I properly calculate the ampacity of this proposed circuit? It runs in cable tray for 600', then goes under ground in conduit for 25' where it enters the main sub station. I know it will require additional conduit and termination space. What other items do I need to consider or be concerned about? I don't want the electrical contractor to be my only source of council on this. Thanks!