Let's say that after correcting for ambient temperature and bundling, you end up with an allowable ampacity of 70 amps for #6 THHN (using the 90C rating in table 310.15(B)(16)). However, the terminal lugs in the circuit are only 75C-rated, so the load (if noncontinuous) must be 65 amps or less (according to table 310.15(B)(16)). Is this correct?