Ampacity Derating Question (4), 7ft, 250kcmil THHN, 75° Termination, Underground RMC
Longarch
Chattanooga, TN
Instructor
I'm not following the answer given for an ampacity derating question, which is 255A.
What is the ampacity of (4) 250 kcmil THHN copper current-carrying underground feeders enclosed in a 7 foot riser of rigid metal conduit and terminated on 75°C lugs?
I understand that 310.16, 310.15(C)(1)(c), and 110.14(C) are applied but I'm not understanding the entirety of how.
310.15(C)(1)(c) states adjustment factors shall not apply in this case. So I do not derate at 80% for the quantity of 4 conductors.
Is my answer adjusted per 310.15(B)(1) due to 75° temperature?
They don't give a ambient temperature for temperature correction...the 75°C is the lug rating.
Also, THHN can't be used for underground feeders.
Sounds like the question is trying to trip you up on the 4 current-carrying conductors, but as you've noted 310.15(C)(1)(c) doesn't require adjustment factors for the conductors, so the answer is 255A per T310.16.
Thank you. That's what I thought but I desired verification. ;)