Longarch
Member
- Location
- Chattanooga, TN
- Occupation
- Instructor
I'm not following the answer given for an ampacity derating question, which is 255A.
What is the ampacity of (4) 250 kcmil THHN copper current-carrying underground feeders enclosed in a 7 foot riser of rigid metal conduit and terminated on 75°C lugs?
I understand that 310.16, 310.15(C)(1)(c), and 110.14(C) are applied but I'm not understanding the entirety of how.
310.15(C)(1)(c) states adjustment factors shall not apply in this case. So I do not derate at 80% for the quantity of 4 conductors.
Is my answer adjusted per 310.15(B)(1) due to 75° temperature?
What is the ampacity of (4) 250 kcmil THHN copper current-carrying underground feeders enclosed in a 7 foot riser of rigid metal conduit and terminated on 75°C lugs?