Is there a spot in the code that allows you to run higher ampacities than normal if you are only feeding one piece of equipment? Someone told me there was but I can’t find anything.
Yes, you are correct. Running a larger OCPD to smaller conductors.Can you provide some more information, what do you mean by "higher ampacities" are you referring to an OCPD size greater than than the conductor size?
I don’t remember the particulars, but it was for a condenser for An AC unit. I opted to size everything the normal way. Just wondering what exceptions I can use next time.?hvac application?
What do you want to do?
What code are allows this? 430 motors, 440 A/C units or somewhere else?An example-- Heat pump with a minimum circuit ampacity of 12 amps but a max cir. ampacity of 25 amps. 14 gauge wire is all you need with a 25 amp breaker
What code are allows this? 430 motors, 440 A/C units or somewhere else?
What code are allows this? 430 motors, 440 A/C units or somewhere else?