Ampacity for for 105°C and 125° Low voltage wire

Status
Not open for further replies.

GlenB

Member
Hello,

In the telecom industry we deal primarily with 105°C and occasionally 125°C wire. The NEC tables do not provide any ampacity ratings for these conductor temp's. We have researched this many times and have always found conflicting information.

Is there an NEC approved Formula/Table that will provide the Ampacities for this wire?


Glen Bell
Purcell Systems
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
There are more tables past 310.15(B)(16) which have higher temp rating. For instance 310.15(B)(18) has temp. up at 250C
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If the terminations are covered by the NEC, it really doesn't mater because, in most cases the circuit ampacity will be limited by the 75°C rating of the termination at the equipment.
 

pv_n00b

Senior Member
Location
CA, USA
NEC 310.15(C), conductor ampacity can be calculated under engineering supervision. That's about all the NEC has to offer for those temperature ratings.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
NEC 310.15(C), conductor ampacity can be calculated under engineering supervision. That's about all the NEC has to offer for those temperature ratings.

But as Don said, it doesn't matter what ampacity you calculate. The current is going to be limited to whatever temperature will cause the cable, and thus termination to reach 75 Deg C.
 