I know there is a requirement that indicates for conductors less than 100A, you use the 60C column in 310.15(B)(16) (2014) but I can never locate it. Can anyone help me out?

Thanks,

Steve
 
110.14(C)(1)(a) looks pretty straight forward to me. Am I missing something?

Thanks,

Steve
Note where it says "Unless the equipment is listed and marked otherwise,", most modern equipment has the temperature rating marked on it.

Roger
 
And most that modern equipment is marked 75C also.

Especially circuit breakers, motor controllers and similar equipment.
 