JMeyer2020
Member
- Location
- USA
- Occupation
- Electrical Engineer
I want to verify the ampacity of an installation that uses 750kcmil 1/C CU 15kV cables running through an underground ductbank. There are two feeds in parallel (a total of six cables). Each 1/C cable is installed in its own separate conduit in the ductbank (a total of six ducts).
Unfortunately, I cannot find a rating for a single 1/C cable in an underground duct anywhere!
The cable's datasheet only gives ampacities for triplex installations. I tried going to the NEC Article 315, but I run into the same problem - Tables 315.60(C)(11) through (14) all describe three current carrying conductors together in one duct/conduit (either three 1/C cables, or a single 3/C cable).
I feel pretty confident that with the conductors being isolated they could safely carry more than 565A at 90C... but I don't know the calculations to prove it. Can anyone help?
Unfortunately, I cannot find a rating for a single 1/C cable in an underground duct anywhere!
The cable's datasheet only gives ampacities for triplex installations. I tried going to the NEC Article 315, but I run into the same problem - Tables 315.60(C)(11) through (14) all describe three current carrying conductors together in one duct/conduit (either three 1/C cables, or a single 3/C cable).
I feel pretty confident that with the conductors being isolated they could safely carry more than 565A at 90C... but I don't know the calculations to prove it. Can anyone help?