I am running 25 ft of 3-500MCM/phase from Padmount Tfmr to a Crypto mining container that has a cable entry point 8 ft above grade. So, 17 ft of the conductors will be in buried conduit and the remaining 8 ft will extend vertically above grade to the cable entry point. Since more than 10% of the Total circuit length is in above-grade conduit, outdoors, and therefore different ambient temperature, NEC requires the use of the lower ampacity. Question; does the NEC distinguish between above and below-grade conduits?
We ran some calculations in SKM and it appears that the heat doesn't dissipate in conduit above grade like it does 3 ft in the Earth. But do i really need to de-rate for 8 ft of above-grade conduit?
We ran some calculations in SKM and it appears that the heat doesn't dissipate in conduit above grade like it does 3 ft in the Earth. But do i really need to de-rate for 8 ft of above-grade conduit?