Per table 310.15 (B) (16)----under the 75 deg column #12 can carry 25 amps, But, it has 2 asterisk symbols, and refers you to 240.4 (D) (5)--12 AWG copper 20 amp.
I understand that #12 THHN copper at 75 deg, can only handle 20 amps. per the NEC. Question, I am interpreting that correctly, and anything higher like 25 or 30
amp breaker would be in violation of the NEC, and pose a probable electrical hazard???.
Thank you, for any and all formation.