Hello forum
I just need to be sure that I have understood the NEC correctly, as I am a European citizen!
A 3 conductor feeder cable - Size 4/0 - Temp 90°C/194°F - feeds, for example, a Single Phase installation.
The cable can handle 260A (NEC 310.16)- is this correct?
A similar feeder cable with 4 conductors - for example for use of 3PH + Neutral - must the ampacity be reduced 20 % due to the extra conductor.
So max 208A (NEC 310.15(C)(1))- is this also correct?
We disregard other factors such as ambient temperature etc.
Thanks to all,
Lars Holm