K ktm400sx Member Feb 27, 2006 #1 Iam trying to find a spec for the current carrying capacity of aluminum busbar. This particular bus is 4" x 1/2" Thanks for any help
Iam trying to find a spec for the current carrying capacity of aluminum busbar. This particular bus is 4" x 1/2" Thanks for any help
B bphgravity Senior Member Location Florida Feb 27, 2006 #2 Re: Ampacity of Aluminum busbar Check out 366.23(A) of the 2005 NEC.
mario Senior Member Location Alaska Feb 27, 2006 #4 Re: Ampacity of Aluminum busbar Originally posted by bphgravity: Check out 366.23(A) of the 2005 NEC. Click to expand... I did and it was about gutter ... ????
Re: Ampacity of Aluminum busbar Originally posted by bphgravity: Check out 366.23(A) of the 2005 NEC. Click to expand... I did and it was about gutter ... ????
B bphgravity Senior Member Location Florida Feb 27, 2006 #5 Re: Ampacity of Aluminum busbar Read the whole section...
mario Senior Member Location Alaska Feb 27, 2006 #6 Re: Ampacity of Aluminum busbar 700 amps / sq in ... ok now I can read ... m ...