Ampacity of conductor

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Nec 2014 Table 310.15(B)(16) has two stars next to #10 awg. #10 AWG copper conductor THHW or THWN minimum ampacity is it 30A or 35A?
 
The ampacity is 35. It can't be protected at more than 30A, except where permitted in 240.4(E) & (G).
Ok. So lets say I have 12 current carrying conductors sized #10 AWG THHW or THWN in one conduit. Lowest ampacity you say is 35A. Per Table 310.15(B)(3)(a):

35A*0.5 = 17.5A

so I can use 20A breaker or 15A breaker to protect the cables?

Sent from my SM-G935U using Tapatalk
 
Ok. So lets say I have 12 current carrying conductors sized #10 AWG THHW or THWN in one conduit. Lowest ampacity you say is 35A. Per Table 310.15(B)(3)(a):

35A*0.5 = 17.5A

so I can use 20A breaker or 15A breaker to protect the cables?

Sent from my SM-G935U using Tapatalk

Actually you can use the 90C rating since the wire is 90C and derate from there

40 * .5 = 20 amps
 
Ok. So lets say I have 12 current carrying conductors sized #10 AWG THHW or THWN in one conduit. Lowest ampacity you say is 35A. Per Table 310.15(B)(3)(a):

35A*0.5 = 17.5A

so I can use 20A breaker or 15A breaker to protect the cables?

Sent from my SM-G935U using Tapatalk

Could be a 20A breaker per 240.4(B),

Unless its a branch circuit supplying more than one receptacle. Then it would have to be a 15A breaker per 240.4(B)(1).
 
Could be a 20A breaker per 240.4(B),

Unless its a branch circuit supplying more than one receptacle. Then it would have to be a 15A breaker per 240.4(B)(1).
I do have branch circuits. Each branch circuit has 2 current carrying conductors and their are 6 total branch circuits in one conduit upto power pole. Each branch circuit is going to supply two L5-15 receptacles. Each branch circuit has max load of 10 amps. The receptacles are use for plugging in spot merchandiser.

240.4(B) it would have to be 15A I guess. However, Nec 2014 210.21(B)(2) says to use Table 210.21(B)(2) and for max load 10 I can use 15A or 20A circuit rating. Meaning breaker can be 15A or 20A.

Is their a discrepancy between 210.21(B)(2) and 240.4(B) or am I missing something?

Sent from my SM-G935U using Tapatalk
 
Last edited:
I do have branch circuits. Each branch circuit has 2 current carrying conductor and their are 6 total circuits. Its power pole going to spot merchandiser with each branch circuit supplying two L5-15 receptacles. Each branch circuit has max load of 10 amps.

With locking receptacles, you could maybe argue that you don't have cord-and-plug-connected portable loads, so 240.4(B)(1) doesn't apply. But with 10A loads, why not just go with the 15A circuit.


240.4(B) it would have to be 15A I guess. However, Nec 2014 210.21(B)(2) says to use Table 210.21(B)(2) and for max load 10 I can use 15A or 20A circuit rating. Meaning breaker can be 15A or 20A.

Is their a discrepancy between 210.21(B)(2) and 240.4(B) or am I missing something?

I'm not quite following you, but I don't see any discrepancy between 210.21(B)(2) and 240.4(B). They are talking about different things.
 
With locking receptacles, you could maybe argue that you don't have cord-and-plug-connected portable loads, so 240.4(B)(1) doesn't apply. But with 10A loads, why not just go with the 15A circuit.




I'm not quite following you, but I don't see any discrepancy between 210.21(B)(2) and 240.4(B). They are talking about different things.

Went back and looked. It is locking type so i guess cord and plug does not apply.


However if it were cord and plug then Table 210.21(B)(2) says max load of 12 circuit rating can be 20A or 15A so I am assuming breaker can be 15A or 20A while 240.4(B)(1) says it would have to be 15A.

Sent from my SM-G935U using Tapatalk
 
Went back and looked. It is locking type so i guess cord and plug does not apply.


However if it were cord and plug then Table 210.21(B)(2) says max load of 12 circuit rating can be 20A or 15A so I am assuming breaker can be 15A or 20A while 240.4(B)(1) says it would have to be 15A.

Table 210.21(B)(2) says that the maximum load connected to any 15A receptacle is 12A. It doesn't say anything about protecting the conductor at its ampacity, like 240.4(B)(1) does.

210.21(B)(2) and 240.4(B) talk about completely separate matters. There is no discrepancy between them.


As far as 240.4(B) and locking receptacles, you would have to check with the AHJ to see how they feel about it.
 
Table 210.21(B)(2) says that the maximum load connected to any 15A receptacle is 12A. It doesn't say anything about protecting the conductor at its ampacity, like 240.4(B)(1) does.

210.21(B)(2) and 240.4(B) talk about completely separate matters. There is no discrepancy between them.
What does Table 210.21(B)(2) mean by Circuit Rating? I thought for branch circuits, circuit rating is determine by branch overcurrent protection size. The table says for max 12A load circuit rating can be 15 or 20A.

Sent from my SM-G935U using Tapatalk
 
What does Table 210.21(B)(2) mean by Circuit Rating? I thought for branch circuits, circuit rating is determine by branch overcurrent protection size. The table says for max 12A load circuit rating can be 15 or 20A.

Sent from my SM-G935U using Tapatalk

Let me try it this way....

210.21(B)(2) says the maximum load on any 15A receptacle of a multi-receptacle circuit is 12A.

210.21(B)(2) also says that the multiple 15A receptacles can be on a 15A branch circuit or a 20A branch circuit.

240.4(B)(1) says that the conductor ampacity on the 15A multi-receptacle branch circuit must be at least 15A, and that the conductor ampacity on the 20A multi-receptacle branch circuit must be at least 20A.
In other words, no "next higher standard overcurrent device rating" allowed for the multi-receptacle circuits.
 
Let me try it this way....

210.21(B)(2) says the maximum load on any 15A receptacle of a multi-receptacle circuit is 12A.

210.21(B)(2) also says that the multiple 15A receptacles can be on a 15A branch circuit or a 20A branch circuit.

240.4(B)(1) says that the conductor ampacity on the 15A multi-receptacle branch circuit must be at least 15A, and that the conductor ampacity on the 20A multi-receptacle branch circuit must be at least 20A.
In other words, no "next higher standard overcurrent device rating" allowed for the multi-receptacle circuits.
I guess question boils down to lets say I have 15 amp rated multi-receptacles with max loading of 12A branch circuit and look at Table 210.21(B)(2) then I can have circuit rating of 15A or 20A. Correct.

How does NEC define circuit rating for branch circuit? Is it just branch conductor ampacity or is it overcurrent protection size? And if it is overcurrent protection device then I can use 20A but 240.4(B)(1) says to use 15A. Would that not be two different directions?

Sent from my SM-G935U using Tapatalk
 
I guess question boils down to lets say I have 15 amp rated multi-receptacles with max loading of 12A branch circuit and look at Table 210.21(B)(2) then I can have circuit rating of 15A or 20A. Correct.

How does NEC define circuit rating for branch circuit? Is it just branch conductor ampacity or is it overcurrent protection size? And if it is overcurrent protection device then I can use 20A but 240.4(B)(1) says to use 15A. Would that not be two different directions?

Sent from my SM-G935U using Tapatalk

Its the overcurrent protection size, if your on the 2017 NEC see 210.18. As Dennis pointed out in post #4 you can use the 90C column for derating your #10 THHN's.
 
Ok. So lets say I have 12 current carrying conductors sized #10 AWG THHW or THWN in one conduit. Lowest ampacity you say is 35A. Per Table 310.15(B)(3)(a):

35A*0.5 = 17.5A

so I can use 20A breaker or 15A breaker to protect the cables?

Sent from my SM-G935U using Tapatalk

U R derating, so u can use the 90 degree column which is #10 is rated for 40A
 
Its the overcurrent protection size, if your on the 2017 NEC see 210.18. As Dennis pointed out in post #4 you can use the 90C column for derating your #10 THHN's.
I have 75 degree termination and insulation.

lets say I have 15 amp rated multi-receptacles with max loading of 12A branch circuit and look at Table 210.21(B)(2) then I can have circuit rating of 15A or 20A. Correct.

I can use 20A but 240.4(B)(1) says to use 15A. The two NEC 2014 articles their is discrpenancy one is saying only 15A other says I can use 20A?? Am I missong something?

Sent from my SM-G935U using Tapatalk
 
I have 75 degree termination and insulation.

lets say I have 15 amp rated multi-receptacles with max loading of 12A branch circuit and look at Table 210.21(B)(2) then I can have circuit rating of 15A or 20A. Correct.

I can use 20A but 240.4(B)(1) says to use 15A. The two NEC 2014 articles their is discrpenancy one is saying only 15A other says I can use 20A?? Am I missong something?

Sent from my SM-G935U using Tapatalk

Step 1 determine the rating of your OCPD; you stated you have 10AWG THWN rated 75C not THWN-2 or something?
So you derated to 17.5A
240.4(B)(1) is telling you you cant round up when you are working with a circuit with more than one receptacle supplying cord and plug connected portable loads. And thats what you have so your OCPD is 15A.
Step 2 Pick your receptacle
2014 NEC 210.21(B)(2) Is saying a 15A receptacle shall not supply a load more than 12 Amps, and that 15A receptacle is permitted to be connected to a 15 or 20 amp branch circuit.
 
240.4(B)(1) is telling you you cant round up when you are working with a circuit with more than one receptacle supplying cord and plug connected portable loads. And thats what you have so your OCPD is 15A.
Step 2 Pick your receptacle
2014 NEC 210.21(B)(2) Is saying a 15A receptacle shall not supply a load more than 12 Amps, and that 15A receptacle is permitted to be connected to a 15 or 20 amp branch circuit.

Thats the thing 210.21(B)(2) is telling me circuit rating is permitted to be 15A or 20A but that contradicts what 240.4(B)(1) is telling me that circuit rating needs to be 15A not permitted to be round up to 20A.
 