thunder15j
Member
- Location
- Cali
I have a customer that needs more electrical power to his portable plant. It is not practicle to run new heavier conductors to the plant. The existing feed consists of a paralled 535 MCM diesel locomotive single conductor(6 hot conductors + 2 grounds) feeding a portable plant from a 1200 amp breaker. Conductors are laying on the ground or in some places they have been covered with clean rock free native soil. The single conductor cords also have either USE or RHW stamped one them (memory lapse).
I cannot find cable/cord ampacities in NEC art 400, but cable manufactures show ampacity of 737 amperes @ good old 90 degrees C. Obviously I cannot land these wires under a breaker and use that rating. However, since the wires (535 MCM) are landed on lugs (most lugs are 90 C) bolted to busbar and then other higher rated wires are cabled from busbar to breaker on both ends, I feel I can use the 90 degree C.
I was thinking of installing a 1600 amp 100% continuous duty breaker with a 1400 amp trip unit to replace the 1200 amp breaker. Wire ampacity would be 2 x 737 = 1474 amps. There are other considerations such as voltage drop, ground wire sizing, and last but not least costs.
Please hit me with some comments. thnx
I cannot find cable/cord ampacities in NEC art 400, but cable manufactures show ampacity of 737 amperes @ good old 90 degrees C. Obviously I cannot land these wires under a breaker and use that rating. However, since the wires (535 MCM) are landed on lugs (most lugs are 90 C) bolted to busbar and then other higher rated wires are cabled from busbar to breaker on both ends, I feel I can use the 90 degree C.
I was thinking of installing a 1600 amp 100% continuous duty breaker with a 1400 amp trip unit to replace the 1200 amp breaker. Wire ampacity would be 2 x 737 = 1474 amps. There are other considerations such as voltage drop, ground wire sizing, and last but not least costs.
Please hit me with some comments. thnx