According to 310.15, the ampacity of a conductor is calculated to carry
current CONTINUOUSLY without getting damage, so why do I have to multiply
125% to the ampacity of the continuous load when I size the wire for my
branch circuit.

Thank you.
 
Good question. :happyyes: Wish I had a good answer. :happysad: Best I can offer is that it might be because the terminations are not able to handle the same current continuously without overheating.

Welcome to the forum.
 
Circuit breaker crowded together in a panel board trap heat which can lower their trip curve.

Yup, that's why equipment that is designed to operate at 100% continuous is listed for continuous operation. {210.19(A)(1)Exception}
 