I found the post at: http://forums.mikeholt.com/showthread.php?t=85410 but it seems to have a few conflicting answers.
Here are my observations:
NFPA 79 Electrical Standard for Industrial Machinery: "The provisions of this standard shall apply to the electrical/electronic equipment, apparatus, or systems of industrial machines operating from a nominal voltage of 600 volts or less, and commencing at the point of connection of the supply to the electrical equipment of the machine." I assume this means it includes the industrial control panel.
UL 508A Standard for Industrial Control Panels: This applies if we want to be listed or claim compliance as UL listed. It is good guidance, if you have it, but sizing conductors on the safe side will always keep you in the clear.
The NEC (NFPA 70) does not apply inside the panel.
My questions:
Ampacity requirements for wires are still that the over-current protective device is less than the ampacity of all downstream wires after all deratings are applied, correct?
I don't have the reference but in the NEC (maybe in NFPA 79, as well) there is a paragraph that states, as close as I can remember, "Any circuit protected by a 20A breaker or less shall be considered" ... protected for any wire size. Does that ring a bell with anyone and is that a correct interpretation?
Thanks in advance! I'm still trying to convince my boss that my time digging through the free online versions of NFPA isn't worth the $200 or so bucks.:happysad:
Here are my observations:
NFPA 79 Electrical Standard for Industrial Machinery: "The provisions of this standard shall apply to the electrical/electronic equipment, apparatus, or systems of industrial machines operating from a nominal voltage of 600 volts or less, and commencing at the point of connection of the supply to the electrical equipment of the machine." I assume this means it includes the industrial control panel.
UL 508A Standard for Industrial Control Panels: This applies if we want to be listed or claim compliance as UL listed. It is good guidance, if you have it, but sizing conductors on the safe side will always keep you in the clear.
The NEC (NFPA 70) does not apply inside the panel.
My questions:
Ampacity requirements for wires are still that the over-current protective device is less than the ampacity of all downstream wires after all deratings are applied, correct?
I don't have the reference but in the NEC (maybe in NFPA 79, as well) there is a paragraph that states, as close as I can remember, "Any circuit protected by a 20A breaker or less shall be considered" ... protected for any wire size. Does that ring a bell with anyone and is that a correct interpretation?
Thanks in advance! I'm still trying to convince my boss that my time digging through the free online versions of NFPA isn't worth the $200 or so bucks.:happysad: