I have been hired to evaluate the main service for a manufacturing facility, there typical installation is an underground feeder from the utility to the main transformer primary side, the secondary side is routed through a concrete manufactured wireway with steel plates covering it. The feeder cables consist of XHHW-2 cables laid inside this wireway as individual feeders, the transformer produces a 4000a secondary, they have installed 8 sets of 4 #750 for the service. If I use the open air ampacity then they are correct, but these feeders have not been segregated into sets of 4 but just all laid in the tray and I do not feel they meet the open air requirement installation to allow the extra ampacity. Article 392 for cable tray list specific requirements, when researching the code I find that the cables are to configured in a triangular fashion and 'spaced' apart from each set a distance equal to the width of the bundled conductors. Am I correct, they have applied the open air ampacity where in fact they do not meet the criteria just on spacing let alone that its in a concrete covered trench?