JonathanEngr
Member
- Location
- North Carolina, USA
- Occupation
- Professional Engineer
Hi, everyone. I have a circuit that was installed a few years ago, and the wire is 12 gauge THHN wire in conduit with two conductors, a neutral and a ground. The wires are connected to a 30A breaker, and I've been told that's acceptable since there's no reduction due to there being less than 3 conductors in the conduit. At the same time I've been told that the 30A rating in the NEC manual is for derating purposes only, and that 12 gauge wire can only have a 25A breaker max. I was also told by others that under no circumstances can 12 GA wire be used with more than a 20A breaker.
Can someone de-mystify the NEC code and allowable current in the wire? Thanks!
Can someone de-mystify the NEC code and allowable current in the wire? Thanks!