roshan1430
Member
- Location
- Los Angeles, CA
Hi Guys, I have an unique situation here. I am Designing a 2400V cable run from Xmer to MCC through 100ft long duct-bank. My FLA comes to 902.2 and after 125% it gives me 1127.65 amp. I am planning to have 3 parallel run. So if I use 500 MCM cable I get 375 amp each conductor or 1125 amps for my 3 parallel run(NEC table 310.60(C)(77). It puts me 2.65 amp below my required ampacity. Is there a NEC code which help me deal with the situation. I am trying avoid to go to next up 750 MCM which will be too big unnecessarily. Am I referring to correct table ? Thank you.