Re: ampacity
Ronald had the answer. The surface area (circumference) does not increase as fast as the cross section (circular mils). The cross section carries the current and generates the heat. The surface area gets rid of the heat.
Circumference = pi x 2 x radius = pi x diameter.
Area = pi x radius squared.
Double the diameter of the cable and the cross section area goes up 4 times. Surface area only doubles.
So you have 4 times as much copper but only twice as much jacket area to let out the heat.
500 kcmil has twice the copper of 250 kcmil but only 41% more surface area (circumference). 250 copper Class B compact diameter = 0.520", 500 diameter = 0.736".
As Jim pointed out, skin effect also increases the effective resistance, (about 7%) so there is more heat to get out of a smaller area.
Bob Wilson, P.E.
Edited to add conductor diameters.
[ July 21, 2005, 12:11 PM: Message edited by: rcwilson ]