C crawler Member Jul 9, 2004 #1 My question is... Article 310-16. What column do I use for the service subfeed load side of the meter? What size wire for 600 amps? (Southwest Ranches--close to Davie Florida) Thanks, crawler
My question is... Article 310-16. What column do I use for the service subfeed load side of the meter? What size wire for 600 amps? (Southwest Ranches--close to Davie Florida) Thanks, crawler
V vinnyrpb Member Jul 9, 2004 #2 Re: Ampacity That would be the 75? Column for us Florida guys......with parallel 350's for 600 Amps [ July 09, 2004, 03:20 PM: Message edited by: vinnyrpb ]
Re: Ampacity That would be the 75? Column for us Florida guys......with parallel 350's for 600 Amps [ July 09, 2004, 03:20 PM: Message edited by: vinnyrpb ]
ryan_618 Senior Member Location Salt Lake City, Utah Jul 9, 2004 #4 Re: Ampacity You could use parallel 300's if the computed load is less than 570 Amps. 240.4(B), 230.42
Re: Ampacity You could use parallel 300's if the computed load is less than 570 Amps. 240.4(B), 230.42