I'm working on a project, where the incoming voltage is 480 volt 3 phase 4 wire.
We are going to run (9) 277 volt single phase heaters and balance them over the 3 phase power.
Total wattage is 27,195 watts. each 277 volt circuit will pull 10.9 amps roughly.
How do I determine the actual load amps for the 480 volt incoming breaker?
In the past I've used the 277 volt amps actually on each leg, (or in this case roughly 33 amps) and added 25% but there should be a formula for the total load amperage.