meterchick
Member
- Location
- Ulysses, Kansas, USA
We have a 100 HP motor on a 112.5 kVA transformer with a Benshaw VFD 277/480 Y, the consumer called in about the transformer being hot. We IRed the transformer and found it to be about 188 F which was 60 F hotter than other similarly sized and loaded transformers in the area. Amperage measured in the electric meter is running about 25 A which seemed low, but I thought maybe he doesn't have it running that hard. We checked amperage in the transformer, meter can, and his disconnect. All of these readings are running 70 to 90 amps, unevenly loaded, which matches the readings on the VFD. A phase is leading where B and C are lagging with no amperage whatsoever on the neutral. We then hooked up a three phase recorder and initial readings are showing Power Factor to be +14, -34, -96 ABC respectively. I don't understand how this is possible. Could this be a harmonics problem?? Any ideas would be welcome, I am totally stumped on this one!!