Good afternoon,
i have a situation on a project where we are being blamed for the green water stains in the toilets being caused by electrolysis. This is a large service and a large building. We have a 2000a 3phase 208v MDP with 23 separate sub panels throughout the house, not including lighting control panels. We have parallel feeders coming into the house with ground wires sized to the feeders.(6 sets) Putting a clamp on meter on the ground wire at the MDP gives me a variable reading anywhere between 1.2 and 4.9 amps, but I can get no voltage reading using the same method.
As I turn off equipment, the reading goes down...
is this normal and is it a cause for the electrolysis?
i have a situation on a project where we are being blamed for the green water stains in the toilets being caused by electrolysis. This is a large service and a large building. We have a 2000a 3phase 208v MDP with 23 separate sub panels throughout the house, not including lighting control panels. We have parallel feeders coming into the house with ground wires sized to the feeders.(6 sets) Putting a clamp on meter on the ground wire at the MDP gives me a variable reading anywhere between 1.2 and 4.9 amps, but I can get no voltage reading using the same method.