I have a 400A 480Y/277/4W panel and a 225A 208Y/120/4W panel. As of now I have the 480 panel feeding a 75kVA xfmr which then leads to the 208 panel. For the breaker protecting the xfmr I used a 90A 3 pole breaker (75kVA / [480 * sqrt(3)]). Now my real question is how do you calculate the amperage on the 480 side?
225A panel has phase A = 178A, phase B = 189A, and phase C = 182A. When I show the amps used on my 480 panel do I use these values or is there a similar transformation taking place (like how I found the breaker size).
Thanks for the help!